Test certification & changes to supply characteristics

Looking for some guidance please, I am working on a construction site with a large temporary accommodation block due to be occupied asap. Due to design issues the HV/ LV supply has been delayed, to work around this a generator will be utilised as a short term solution. 
This means testing & inspection will be completed via the genset and certs issued, when the new substation is completed the generator will be disconnected and sub-mains will be connected to the permanent LV supply. 
This raises a question regarding re-test, in my experience usually best practice would be a full re-test, but some on the project are suggesting only the sub-mains will require re-testing. 
To me this would probably come down to the designer signing the test cert and what they are prepared to accept, if only re-testing the sub-mains  I would think the final circuits Zs/ Pfc would have to be calculated as the previous test results/certs from the generator would be invalid due to the change of supply characteristics right?

So can anyone offer advice as to the options and is there anything in BS7671 regs that would be relevant to this situation, it’s also worth considering that if a EIC is issued for the generator can there be another issued for the LV supply? Is it possible to issue more than 1 EIC or  update the original or would be a condition report? 
I’ve come across this situation before and it always seems to be a contentious subject with lots of different opinions, sorry for the long winded post, but would really appreciate some professional opinions on this, thanks Pray 

Parents
  • Essentially that is not the problem, but the point with a local substation is making sure the switchgear is rated for the much higher PSCC. If the test cert for use with the generator, I see no reason to retest everything, but the upfront switchgear must be suitable for the mains supply. As the original EIC is presumably satisfactory and BS 7671 only applies after metering, there is no reason for any documentation change, provided my point is met. BS7671 does not cover the supply source as such, although generator supplies have a few points and maybe you should check section 704 for construction sites.

Reply
  • Essentially that is not the problem, but the point with a local substation is making sure the switchgear is rated for the much higher PSCC. If the test cert for use with the generator, I see no reason to retest everything, but the upfront switchgear must be suitable for the mains supply. As the original EIC is presumably satisfactory and BS 7671 only applies after metering, there is no reason for any documentation change, provided my point is met. BS7671 does not cover the supply source as such, although generator supplies have a few points and maybe you should check section 704 for construction sites.