High earth leakage current on earth bar from mobile telecommunication's equipment

I'm reviewing a mobile infrastructure power system where we have recorded (using a clamp meter) 16A on the MET earth and similar readings on the various bonds terminated onto a common 8 way copper bar earth bar. The site has a 300mA RCCB installed at the TN-C-S source which operates fine as expected however the high current running through the exposed copper earth bar in the meter cabinet is a concern. 

It's worth mentioning that the primary load is mobile network equipment which includes rectifiers and understandably will produce earth leakage from the DC systems. I suppose this would be considered 'planned' earth leakage, however the potential for electric shock from an exposed copper bar cannot be ignored.

I had assumed the IET Guide to Data Centre Power Systems would have some solution to DC earth leakage issues, however this has not yet been formally published. I have encountered high earth currents in a previous project (rail) which resulting the DNO repairing a cable joint in the street however this site is rural and the DC tech seems to be the prime suspect. Is there an IET guidance on how this should be dealt with?

**UPDATE**

The final outcome to this was a broken neutral conductor in the supply cable. When the DNO removed the LV earth link to separate the LV & HV earthing systems in line with G78 the supply was completely lost which identified the the system had been using the combined earth system as a return path. The supply was rewired back to the nearest joint and problem solved. 

Parents
  • There is a considerable degree of misunderstanding going on here, why do you think this is DC leakage?. Because there is DC operated equipment with rectifiers etc does not mean that there is any Earth leakage! I agree with the others, this is probably NORMAL PME diverted neutral current due to the site having a better Earth than anywhere else. You also need to be careful that you choose the correct Ammeter, you need one that only measures the DC component, which Hall effect ones are unlikely to do, and ideally you need to measure the spectrum of the leakage current as your equipment may well have mains filtering which may well pass much more 50Hz to Earth than consumer type equipment. As above, measure each of the MET cables separately to assess what is actually happening.

Reply
  • There is a considerable degree of misunderstanding going on here, why do you think this is DC leakage?. Because there is DC operated equipment with rectifiers etc does not mean that there is any Earth leakage! I agree with the others, this is probably NORMAL PME diverted neutral current due to the site having a better Earth than anywhere else. You also need to be careful that you choose the correct Ammeter, you need one that only measures the DC component, which Hall effect ones are unlikely to do, and ideally you need to measure the spectrum of the leakage current as your equipment may well have mains filtering which may well pass much more 50Hz to Earth than consumer type equipment. As above, measure each of the MET cables separately to assess what is actually happening.