High earth leakage current on earth bar from mobile telecommunication's equipment

I'm reviewing a mobile infrastructure power system where we have recorded (using a clamp meter) 16A on the MET earth and similar readings on the various bonds terminated onto a common 8 way copper bar earth bar. The site has a 300mA RCCB installed at the TN-C-S source which operates fine as expected however the high current running through the exposed copper earth bar in the meter cabinet is a concern. 

It's worth mentioning that the primary load is mobile network equipment which includes rectifiers and understandably will produce earth leakage from the DC systems. I suppose this would be considered 'planned' earth leakage, however the potential for electric shock from an exposed copper bar cannot be ignored.

I had assumed the IET Guide to Data Centre Power Systems would have some solution to DC earth leakage issues, however this has not yet been formally published. I have encountered high earth currents in a previous project (rail) which resulting the DNO repairing a cable joint in the street however this site is rural and the DC tech seems to be the prime suspect. Is there an IET guidance on how this should be dealt with?

**UPDATE**

The final outcome to this was a broken neutral conductor in the supply cable. When the DNO removed the LV earth link to separate the LV & HV earthing systems in line with G78 the supply was completely lost which identified the the system had been using the combined earth system as a return path. The supply was rewired back to the nearest joint and problem solved. 

Parents
  • well that is good news. You had not mentioned it was on the side of a pylon and G78 applied - we may have got there rather sooner if you had. Still glad it is resolved - every day is a school day an all that.

    Separation of HV and LV earth can be a mixed blessing, and over time opinion on best practice has ebbed and flowed a bit. It used to be that if the electrodes were less than an ohm to terra-firma then the site was considered 'cold' (rise of earth while clearing largest credible HV side fault acceptable) then combine, and if not, then keep separate and consider the HV side to be 'hot' (rise of earth while clearing largest credible HV side fault gives rise to a dangerous voltage).
    This lead to most pole pig transformers in the sticks being 'hot' and most large substations with big earth arrays or mats rather than one or two rods being considered 'cold'.  The newer and more scientific approach factors in the HV supply characteristics and needs about half a side of maths, to express the earth voltage rise, and then conclude more or less the same except in a few corner cases that probably could have been wired up either way...

    Mike

Reply
  • well that is good news. You had not mentioned it was on the side of a pylon and G78 applied - we may have got there rather sooner if you had. Still glad it is resolved - every day is a school day an all that.

    Separation of HV and LV earth can be a mixed blessing, and over time opinion on best practice has ebbed and flowed a bit. It used to be that if the electrodes were less than an ohm to terra-firma then the site was considered 'cold' (rise of earth while clearing largest credible HV side fault acceptable) then combine, and if not, then keep separate and consider the HV side to be 'hot' (rise of earth while clearing largest credible HV side fault gives rise to a dangerous voltage).
    This lead to most pole pig transformers in the sticks being 'hot' and most large substations with big earth arrays or mats rather than one or two rods being considered 'cold'.  The newer and more scientific approach factors in the HV supply characteristics and needs about half a side of maths, to express the earth voltage rise, and then conclude more or less the same except in a few corner cases that probably could have been wired up either way...

    Mike