High earth leakage current on earth bar from mobile telecommunication's equipment

I'm reviewing a mobile infrastructure power system where we have recorded (using a clamp meter) 16A on the MET earth and similar readings on the various bonds terminated onto a common 8 way copper bar earth bar. The site has a 300mA RCCB installed at the TN-C-S source which operates fine as expected however the high current running through the exposed copper earth bar in the meter cabinet is a concern. 

It's worth mentioning that the primary load is mobile network equipment which includes rectifiers and understandably will produce earth leakage from the DC systems. I suppose this would be considered 'planned' earth leakage, however the potential for electric shock from an exposed copper bar cannot be ignored.

I had assumed the IET Guide to Data Centre Power Systems would have some solution to DC earth leakage issues, however this has not yet been formally published. I have encountered high earth currents in a previous project (rail) which resulting the DNO repairing a cable joint in the street however this site is rural and the DC tech seems to be the prime suspect. Is there an IET guidance on how this should be dealt with?

**UPDATE**

The final outcome to this was a broken neutral conductor in the supply cable. When the DNO removed the LV earth link to separate the LV & HV earthing systems in line with G78 the supply was completely lost which identified the the system had been using the combined earth system as a return path. The supply was rewired back to the nearest joint and problem solved. 

Parents
  • Can the high leakage current be pinned to the nature of loads i.e inductive loads

    Yes and no. Inductive loads as such shouldn't cause protective conductor currents, but many kinds of loads do naturally have relatively high leakage. Likely culprits these days are Class I items with electronic PSUs - as the EMI filters inevitably leak some current to PE. In industrial environments that might include some quite large motors with variable speed or inverter drives. More traditionally you might look for things with less than perfect insulation - e.g. mineral insulated heating elements (e.g. immersion heater or old radiant cooker elements) or even MICC cabling if there's lots of it (especially if the insulation has got damp) and the really old school classic would be the electrode water heater.

       - Andy.