TESTING FOR ABSENCE OF VOLTAGE
In the Project I am working on in Denmark for a global client, the North American Electrical Team are putting together a new bulletin on non-contact voltage testers and want EU to have their input (what do our Regs state).
I was wondering if the statement they are giving aligns with EU/UK standards and if so, can you identify a spec or section of the Regs, please?
Topic: NFPA 70E 120.5(7) TESTING FOR ABSENCE OF VOLTAGE
According to Article 100, an “Electrically Safe Work Condition” is a “state in which an electrical conductor or circuit part has been disconnected from energized
parts, locked/tagged in accordance with established standards, tested to verify the absence of voltage, and, if necessary, temporarily grounded for personnel
protection”.
NFPA 70E does NOT permit using a noncontact type tester (see image) when testing for the absence of voltage on electrical systems rated 1000 volts or less.
Section 120.5(7) specifically requires the absence of voltage test to be conducted from “phase-to-phase” and “phase-to-ground”. This type of testing cannot be
performed with a noncontact tester.
Section 120.5 provides guidelines on how to both establish and verify an electrically safe work condition. See below for more details on absence of voltage testing.
Below is a sample of NFPA 70E. For the complete section, see the actual NFPA
70E text at NFPA.ORG. Once there, click on the free access link to NFPA 70E.120.5
(7) Use an adequately rated portable test instrument to test each phase conductor or circuit part to verify it is deenergized. Test each phase conductor or circuit part both phase-to-phase and phase-to-ground. Before and after each test, determine that the test instrument is operating satisfactorily through verification on any known voltage source.
Exception No. 1: An adequately rated permanently mounted test device shall be permitted to be used to verify the absence of voltage of the conductors or circuit parts at the work location, provided it meets the all following requirements:
(1) It is permanently mounted and installed in accordance with the manufacturer’s instructions and tests the conductors and circuit parts at the point of work;
(2) It is listed and labeled for the purpose of verifying the absence of voltage;
(3) It tests each phase conductor or circuit part both phase-to-phase and phase-to-ground;
(4) The test device is verified as operating satisfactorily on any known voltage source before and after verifying the absence of voltage.
Exception No. 2: On electrical systems over 1000 volts, noncontact test instruments shall be permitted to be used to test each phase conductor.
  • There was an excellent training video on the IET YouTube channel showing the dangers of isolation when there’s diverted neutral currents, showing that although the installation is completely isolated using the main switch and by pulling out the DNO main fuse then proving that there is not any voltage present, disconnecting the main earth conductor will mean that  full mains voltage will be present on exposed conductive parts and “earthed” metalwork such as water and gas pipework, presenting the risks of injury and death from electrocution.
    So along with voltage testers clamp amp meters should be used as part of the safe isolation procedure.
    The IET took the video down, despite it being one of the most informative and best videos on YouTube.
  • Yes - actually a check for 'is current flowing' is  another useful example of a non-contact measurement to make, and a direct connection to measure current is less safe than a non -contact (clamp meter) one as for a direct connection test you have to open circuit a possibly unknown cable before you asses the current flowing.
    But I agree also on the point about the scale of the installation. If you know the whole building is dead, then there is far less risk of interrupting something nasty - but not none - current may come  in on the water pipes and go out on the CPC or something.
    So now we have two none contact tests - one with the E-field probe and one with a magnetic current clamp. In an ideal world one of each would precede dismantling.
    M.
  • https://youtu.be/KmZluT7n9qc
  • The IET took the video down, despite it being one of the most informative and best videos on YouTube.
    Sometimes these things are outside IET's own control. It was referred to from a Wiring Matters article if memory serves correctly ... was it this one: https://electrical.theiet.org/wiring-matters/years/2021/84-march-2021/broken-pen/ ?