Hi, there. I'd like to discuss and find out the appropriate method how to properly design effective main equipotential bonding system in industrial areas like that (pic rando):
Hereinafter all terms as per IEC 60050-195 vocabulary. The system is TN-S.
Just for remembering requirements of standards. In accordance to 410.3.3 IEC 60364-4-41 the automatic disconnection of supply (ADoS) is one of the generally permitted protection measurements.
ADoS is the basic and widely utilized measurement in electrical installations, including industrial areas.
For protection in case of fault among other measurements protective equipotential bonding must be used 411.3.1.2 IEC 60364-4-41. As the basis I've taken equipotential bonding diagram Annex B IEC 60364-5-54, therefore all exposed conductive parts incoming to the building (in such case area) and neutral point of the source shall be equipotentially bonded via protective equipotential conductors to MET (main earthing terminal), which in turn connected to earthing arrangement by mean earthing conductor as well as to neutral point of source trancformer via PE(PEN) wire.
Therefore area's the interconnection diagram of protection wires and conductive parts will be following:
Hence the equipotential zone covers whole area
Did I get it correct, or some points missed?