AFDDs in medical locations

AFDDS are not required in Groups 1 and 2 medical locations and may be employed in Group 0 situations subject to risk assessment. Why the written get out clause specifically for medical situations? Was there someone on JPEL 64 minding the coppers for the NHS, or is there a more technical aspect to this that I am missing? 

Parents
  • More likely, they don't have any guarantees that the things won't nuisance trip when powering unspecified bits of medical equipment.

Reply
  • More likely, they don't have any guarantees that the things won't nuisance trip when powering unspecified bits of medical equipment.