The Main source earth loop impedance is high(with earth fault IDMT) , will the sub-main switch protected by the main switch?

Hello there, I have a question about installation new 63A MCCB when the existing main source earth loop impedance is over the requirement 0.53Ohm. 

I am wondering if the new switch may be able to be protected by the building main switch 400A MCCB with IDMT Earth Fault protection relay.

Sorry for my clumsy English, I have also attached an image for a better explanation. 

Cheers!~

Parents
  • Or simply provide supplementary bonding to the 63A circuit and check energy let-through.  GF protection might be difficult to add to the sub-circuit if it exists as you will also want selectivity with the 400A GF protection. Other than that change from T/M MCCB to electronic and set parameters to suit.

Reply
  • Or simply provide supplementary bonding to the 63A circuit and check energy let-through.  GF protection might be difficult to add to the sub-circuit if it exists as you will also want selectivity with the 400A GF protection. Other than that change from T/M MCCB to electronic and set parameters to suit.