When is a PEI not a PEI?

"Prosumer" Electrical Installation that is - i.e. an installation that can both produce and consume electricity.

I've been looking over the new Part 8.

It seems to describe quite a sophisticated setup - a "smart" system if you like - dynamically changing things according to some pre-programmed algorithms - maybe to minimise imports, perhaps to export 'when the price is right', deciding whether storage (if present) should accumulate or release, or something else. There even seems to be a specific requirement that a PEI incorporate an 'Electrical Energy Management System' (EEMS) (822.4).

Which got me thinking - how does a conventional ("dumb") grid-tied PV system fit into this? - where the amount of power generated locally is uncontrolled (i.e. just depends on external variables such as sunlight) and the only "management" is what can be achieved using a length of copper and Ohm's Law (i.e. any surplus just gets exported).

Is the idea that such installations should be smarter in future, or is it just that the non-existent management system of a typical PV system can just scrape through as a 'minimal' EEMS?

    - Andy.

  • It also begs the question for a TN system why isolate N and leave the c.p.c. connected if they're connected together anyway (typically at the origin) and so likely both be subject to a very similar undesirable voltage compared with terra firma.

       - Andy.

  • well yes, we have noted before that the standards are not good at separating earthed objects that are also metallically connected and those that are earthed only by being stuck into terra-firma. (The obvious example is a  failure to distinguish between bonding to a water pipe that may carry significant diverted current voia a sub-ohm impedance to the neighbours , and to something like a bus shelter that will be  its own electrode of some tens of ohms at least. Both are identically classed as "extraneous conductors" variation in prospective current, and sensible cable size may be significant ..)

    However, if in this case BS7671 actually mean provide an electrode or equivalent buried metal suitable to operate the RCD or what have you, then that needs to be made explicit, and depending on the ADS arrangement, perhaps quite substantial undertaking. I would not have read it that way.

    M.

  • Or in other words a decent earth is needed as ADS must work promptly with all possible combinations of internal and external supply and all the possible variations in Zs and pssc that implies.

    Part 2 defines "Earth" as the conductive mass of the Earth - but the earth loop on a TN system doesn't include The Earth - it's metallic all the way back to the star point. The actual resistance of the system to Earth on a TN system can be reasonably high (anything up to 20 Ohms, often in the region of 1 Ohm) so not really comparable with Zs when you're using overcurrent protective devices, not that the N conductor need any have particular resistance to enable ADS as it's entirely uninvolved.

       - Andy.

  • Do we not think it is just a typo and missing the word 'enough' ?,

    As in "a low enough impedance to ..."

    Or in other words a decent earth is needed as ADS must work promptly with all possible combinations of internal and external supply and all the possible variations in Zs and pssc that implies.

    It could have been clearer, and certainly if that is not what was meant then it really does need to be clarified.

    M

  • way.

    (quite what "connected to Earth by a low resistance to meet the disconnection times..." is supposed to mean is a quite different point of contention)

    Your not the only one, the NICEIC Technical Helpline admitted that they had no idea!

  • I see what you're getting at now ... so there's potentially a debate around whether 'not installed' equates to 'not required' (it could be argued, converse to your assertion, that if I don't need protective bonding in a building, because there are no extraneous-conductive-parts then I have indeed installed protective earthing and bonding to meet the requirements of Regulation Group 411.3.1).

    Arguably, if none of the accessible metal parts are extraneous-conductive-parts, and all others that might be affected by potential are exposed-conductive-parts (or connected to exposed-conductive-parts) then it doesn't really matter.

    So I guess it just depends which perspective you take (or the guidance takes ... GN2 appears to err on the permissive side, for example ... para 2 page 47 of the 9th Ed 2022).

  • Are you sure? There are two lowercase Roman indents in 461.2, and the Neutral need not be isolated if either condition is met, not both.

    As i read it, the requirement that 'protective equipotential bonding is installed and ... ' is in the leading paragraph and so applies either way.

    (quite what "connected to Earth by a low resistance to meet the disconnection times..." is supposed to mean is a quite different point of contention)

      - Andy.

  • yet 461.2 says we need to isolate N

    Are you sure? There are two lowercase Roman indents in 461.2, and the Neutral need not be isolated if either condition is met, not both.

  • Yes, a lot of questions are asked about 'main bonding structures outdoors'

    In the 461.2 context I think the confusion was subtler than that - even in indoor situations it's increasingly common not to have any bonding at all (plastic pipes) - so all the metalwork will either be connected to the MET via c.p.c.s or free to float (i.e. not extraneous) - so just as safe, if not safer, than having a traditional installation with all bonding in place - yet 461.2 says we need to isolate N (as we would in a TT installation in the old days).

       - Andy.

  • I think we knew the intention rather than the words said

    I think it's as simple as the fact that indoors, you transfer potential throughout a building in the wiring and other metallic services, so best to link them all together. Usually outdoors, things come into fortuitous contact with the ground - so the Earth itself provides all the required local bonding (in theory).

    Situations like EV, where the vehicle is potentially insulated from Earth via its tyres, and you might transfer remote Earth potential to it generating a local touch potential with respect to feet (or simultaneously-accessible metallic items in contact with Earth), do make us think again ... BUT if we were to apply 'main bonding' it could well simple generate a touch potential elsewhere (e.g. at the other end of a long metal fence) that wasn't there before. So overall, best to leave well alone. MOre tricky, however, with fences in places where it's necessary to bond fences for other reasons (e.g. HV installations such as substations and railways).