In the latest Wiring Matters issue 93, there is an article on high protective conductor currents and section 543.7.1.
It quotes the methods of complying with reg 543.7.1.203 including "A single protective conductor, meeting regulations 543.2 (relating to conductor type) and 543.3 (relating to preserving electrical continuity), having csa of not less than 10 mm2 (to give a mechanically robust connection)."
The author then goes on to describe typical circuits and then says this about ring final circuits.
"Where a standard ring final circuit is employed, complying with Appendix 15 of BS 7671 (using typically 2.5 mm2 live conductors and 1.5 mm2 cpcs) it can be appreciated that the total csa of all of the live and protective conductors will easily exceed 10 mm2 – hence satisfying regulation 543.7.1.203."
Do others agree that the authors above interpretation is imcorrect? I dont know where they have got the sum of all live and protective conductors from?