Solar Array - Grounding

Hi,

Do solar arrays (the frames) need grounding? The inverters in most cases are DC (and isolated from mains) and indeed micro-inverters are class 2 with isolated DC inputs from the array. 

I think if the installation has a TN-C-S earthing system, connecting the roof frame to ground would potentially cause an issue if there was a PEN fault. 

I haven’t seen any solar installations with dedicated earth spikes, so can only assume they are left ungrounded, or (perhaps naively) connected to a PME earthing system. 

Thanks. 

Parents
  • What about lightning protection? Does having various conducting pieces around increase the risk of strikes?

  • What about lightning protection? Does having various conducting pieces around increase the risk of strikes?

    On buildings with LPS, BS EN 62305 series applies, as required by BS 7671.

    If the building is tall enough, or close to a building with LPS, then changing it by adding PV array on the roof may well alter the requirements for LPS, and/or need for bonding the frames to LPS..

Reply
  • What about lightning protection? Does having various conducting pieces around increase the risk of strikes?

    On buildings with LPS, BS EN 62305 series applies, as required by BS 7671.

    If the building is tall enough, or close to a building with LPS, then changing it by adding PV array on the roof may well alter the requirements for LPS, and/or need for bonding the frames to LPS..