Islanding mode earthing requirements with PME supply to inverter in garage

I have the following situation, in my own house I might add:
TN-C-S single phase PME supply
50A B curve MCB in main distribution board feeds 10mm2 3C (one core used as CPC), SWA cable going to garage ~5m away from the house
In the detached garage there is a consumer unit feeding a 32A type B RCBO for an EV charger and a 32A type A rcbo for an inverter, both 30mA
EV charger has an open PEN detection relay
(I know about the selectivity issue here with the MCB but it's determined not a safety issue, short circuit unlikely. Sockets and lighting on separate 2.5mm supply)

Now the question is, if I want to enable the inverter to work in islanding mode, what earthing provisions do I need to add?
The house is detached and more than 30m away from other houses and metal street furniture
Ze from supply is 0.12 ohm, main fuse 100A
Inverter can perform N-E link and coordinate with changeover switch at incoming supply

Am I right in thinking that I should remain connected to supplies earth but add an earth rod? What impedance requirement should this earth rod have?
I think it's 200 ohm because the inverter is protected by a 30mA RCBO and in connected mode, the supply earth will be sufficient.
I also think the earth rod should be connected to the inverter directly (i.e. downsteam from the rcbo and not upstream) so that the RCD will be able to detect the leakage in islanding mode.

Thanks!

Parents
  • It’s going to be incredibly difficult to wire in a new cable to the MET. The house has been extended so the meter cupboard is right in the middle, can’t easily get a cable out.

    I don't see any great technical problem with connecting the electrode to the MET via the 10mm² c.p.c. in the submain - it's quite common to bond extraneous-conductive-parts to the earth bars in sub-boards,

    If running new cables to the intake position is a non-starter, I do wonder how you're going to make the connection between the inverter control system and the disconnect-from-the-grid contactor though. I suppose a wireless link plus a UPS and the intake might be an option, but I've never heard of it being done that way.

        - Andy.

  • This is a good point. I can get a cat 6 cable in which connects to the energy meter (alternative to CT coil) and that would leave me with 6 twisted signal pairs remaining. The inverter has the ability to send an ELV signal for coordinating islanding mode. I haven’t really thought about how this would be setup. Perhaps a contactor exists which opens when power is lost but to close it again, requires the ELV signal.

Reply
  • This is a good point. I can get a cat 6 cable in which connects to the energy meter (alternative to CT coil) and that would leave me with 6 twisted signal pairs remaining. The inverter has the ability to send an ELV signal for coordinating islanding mode. I haven’t really thought about how this would be setup. Perhaps a contactor exists which opens when power is lost but to close it again, requires the ELV signal.

Children
  • The inverter has the ability to send an ELV signal for coordinating islanding mode.

    The control system needs to do more than "send a signal" - what about failure modes (island mode isolator fails to open or close, same with N-E bond relay)?

    This is why a G99 notification is usually required from the DNO for this type of functionality.

    It's not trivial to do, and consequences of something going wrong are either breach of legislation, or a whole host of electrical safety issues which can be lethal.

  • The inverter has G98 and G99 approval, it's a sunsynk 3.6kW. I know after the grid comes back online it waits a while and does it's checks + gets the timing and order of actions correct so it can't be in a dangerous situation. I will definitely review all of the manual beforehand.

    To be honest, I will probably end up not going with the earth rod idea and just having a single RCD protected socket at the EPS output as it's a lot easier.

  • To be honest, I will probably end up not going with the earth rod idea and just having a single RCD protected socket at the EPS output as it's a lot easier.

    How is the socket-outlet earth maintained if the DNO are working on the system and cut the supply cable? The guidance is not to have a "floating" socket-outlet in island mode - the reasons are stated in the Code of Practice for Electrical Energy Storage Systems.

  • Manufacturer's instructions allow 1 socket for a class ii item only

  • Manufacturer's instructions allow 1 socket for a class ii item only

    Whilst that would be OK, the issues (as stated in the IET Code of Practice) include:

    1. The use of a standard socket-outlet permits the connection by general users of multi-way adaptors, thus enabling more equipment to be connected.
    2. in the UK we don't have 'Class II socket-outlets' to prevent users connecting Class I ... and generally users are unlikely to be aware of the safety issues.

    In reality, though, aren't most people wanting backup going to want to power lighting (OK could be Class II, but more than one device), internet and TV ? The router may have a "safety voltage" power supply, but there are design features of Ethernet that require a controlled discharge to earth to prevent static charging ... and this also causes "fortuitous earthing". Similarly TV etc. - quickly, you get to the point that, sadly, it's no longer a "floating" power supply for a single device.