Islanding mode earthing requirements with PME supply to inverter in garage

I have the following situation, in my own house I might add:
TN-C-S single phase PME supply
50A B curve MCB in main distribution board feeds 10mm2 3C (one core used as CPC), SWA cable going to garage ~5m away from the house
In the detached garage there is a consumer unit feeding a 32A type B RCBO for an EV charger and a 32A type A rcbo for an inverter, both 30mA
EV charger has an open PEN detection relay
(I know about the selectivity issue here with the MCB but it's determined not a safety issue, short circuit unlikely. Sockets and lighting on separate 2.5mm supply)

Now the question is, if I want to enable the inverter to work in islanding mode, what earthing provisions do I need to add?
The house is detached and more than 30m away from other houses and metal street furniture
Ze from supply is 0.12 ohm, main fuse 100A
Inverter can perform N-E link and coordinate with changeover switch at incoming supply

Am I right in thinking that I should remain connected to supplies earth but add an earth rod? What impedance requirement should this earth rod have?
I think it's 200 ohm because the inverter is protected by a 30mA RCBO and in connected mode, the supply earth will be sufficient.
I also think the earth rod should be connected to the inverter directly (i.e. downsteam from the rcbo and not upstream) so that the RCD will be able to detect the leakage in islanding mode.

Thanks!

  • Manufacturer's instructions allow 1 socket for a class ii item only

  • The inverter has G98 and G99 approval,

    I suspect there's more to G99 than just approval for the individual items of equipment - unless it's changed significantly from the old G59 the DNO will want to come out to inspect the overall system and witness that it behaves correctly under a number of adverse conditions. As Graham said, it's all too easy to put together items of  compliant equipment in a non-compliant way.

       - Andy.

  • You're right but this is going to be used as a G98 system which requires notification only. Also don't worry I will be making everything compliant, this is just me getting my bearings correct early. Massive demand for inverters at the moment, might take weeks just to get the equipment.

  • Manufacturer's instructions allow 1 socket for a class ii item only

    Whilst that would be OK, the issues (as stated in the IET Code of Practice) include:

    1. The use of a standard socket-outlet permits the connection by general users of multi-way adaptors, thus enabling more equipment to be connected.
    2. in the UK we don't have 'Class II socket-outlets' to prevent users connecting Class I ... and generally users are unlikely to be aware of the safety issues.

    In reality, though, aren't most people wanting backup going to want to power lighting (OK could be Class II, but more than one device), internet and TV ? The router may have a "safety voltage" power supply, but there are design features of Ethernet that require a controlled discharge to earth to prevent static charging ... and this also causes "fortuitous earthing". Similarly TV etc. - quickly, you get to the point that, sadly, it's no longer a "floating" power supply for a single device.

  • And... I just checked and island mode is not allowed with G98, never mind.

  • Well this was an interesting discussion, thank you for all your replies. I have learnt a lot and will stick to not using any form of islanding mode until I am a lot more experienced in this area.