Is this method of earthing a water pipe permissible?

A house has the main earth terminal block located next to the electricity supply cable in a cupboard in the living room. The water supply is a blue MDPE pipe located in the kitchen that transitions to a copper pipe about 2m before the stop tap.

About 1m away from the earth terminal block are a pair of copper central heating flow and return pipes. These same two pipes are located right next to the copper water supply pipe in the kitchen.

The easiest, and most economical on cable, method to earth the pipes is to connect the earth terminal block to the central heating pipes in the living room, then connect the central heating pipes to the water supply pipe in the kitchen.

Is this permissible, or must a long length of earth cable be installed under the floorboards connecting the earth terminal block to the water supply pipe?

Parents
  • If I have this correctly, your mains water copper pipe is near the MET, along with the copper flow/return CH pipes yes? So why can you not just run from the MET to the MWS pipe, then run a unbroken loop from that to the CH pipes?

    The CH pipes will most likely be already bonded via the cpc in the supply cable to the boiler/heater but it does no harm to bond them all together where the MWS (main water supply) pipe comes in.

Reply
  • If I have this correctly, your mains water copper pipe is near the MET, along with the copper flow/return CH pipes yes? So why can you not just run from the MET to the MWS pipe, then run a unbroken loop from that to the CH pipes?

    The CH pipes will most likely be already bonded via the cpc in the supply cable to the boiler/heater but it does no harm to bond them all together where the MWS (main water supply) pipe comes in.

Children
  • The MET is quite far away from the MWS. That's why I enquired about using the central heating pipes to connect the two together.