The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Is this method of earthing a water pipe permissible?

A house has the main earth terminal block located next to the electricity supply cable in a cupboard in the living room. The water supply is a blue MDPE pipe located in the kitchen that transitions to a copper pipe about 2m before the stop tap.

About 1m away from the earth terminal block are a pair of copper central heating flow and return pipes. These same two pipes are located right next to the copper water supply pipe in the kitchen.

The easiest, and most economical on cable, method to earth the pipes is to connect the earth terminal block to the central heating pipes in the living room, then connect the central heating pipes to the water supply pipe in the kitchen.

Is this permissible, or must a long length of earth cable be installed under the floorboards connecting the earth terminal block to the water supply pipe?

Parents
  • However an  “insulated” sections of pipe breaking the electrical continuity on extraneous pipework entering a building is no longer permissible if there lead, steel or copper coming out of the ground into a building it needs a Main Protective Bonding conductor, rather than just a few millimetres of plastic pipe and/or fittings before reverting to metal.

  • I would be testing at 500 volts dc after temporary removal of the boiler cpc from the pipe work to the MET,this will prove whether its an extraneous-conductive-part or not . The value i use is 23 K ohms which would allow 10 ma . GN8 describes this process 

  • I assume you are looking at 544.1.2.  The wording has not changed in my copy of BS7671 andt 2, are you referring to the latest GN8?

Reply
  • I assume you are looking at 544.1.2.  The wording has not changed in my copy of BS7671 andt 2, are you referring to the latest GN8?

Children
No Data