Best solution for primary distribution in residential property

I am looking at a project in a fairly large residential property and trying to avoid a collection of small consumer units near the supply head.

Supply is TNCS, no measurements at this stage

The supply head is in an external meter box, I will be putting an additional box of some sort next to it.

Based on a rough initial plan, from the meter head there will be the following connections

60A sub main on 16mm SWA to main house DB

60A sub main on 16mm SWA to garage, feeding two EV chargers with load management on main feed and garage submain.

Assuming 16A connection on 10mm cable to solar panels in field 30 to 50m away

Assuming 16A connection to battery inverter 5m away

House is on fused connection taken from henley blocks in main meter box, plan to leave this as it is and then run tails from henley blocks to second meter box.

Question is what do I do there to support the 3 connections

Initial thought has been an IP65 enclosure with 3 MCB's, but then I have some concerns

  • I don't think I can get an IP65 enclosure with a busbar capable of supporting 16mm cable for the load and MCB's for each of the circuits, with spare slots for future expansion
  • Cables will be armoured clipped direct or underground in ducting
  • Beginning to think a fused switch  might be better for the garage to provide better selectivity, downside is that I will end up with an enclosure for each submain?

VD on garage submain 1.36% and for a 63A fuse with 5 second disconnect time max earth fault loop impedance is achievable at 1.07 ohms. DB in garage will be all RCBO. Garage will be a TT island

Solar and battery system not my responsibility but trying to take a holistic view on design of distribution at the supply head

Are there better ways to do this, enclosures that support cartridge fuses and circuit breakers, just go with metal CU in IP65 enclosure.

Given that the meter head is actually in an open log store next to the house I am swaying towards everything going inside a metal IP65 enclosure

Welcome your thoughts

Parents
  • I cannot see it of course, but another thought may be, depending how much space there is, and how damp it may get, would a second meter box next to the first one look too silly? Once inside that you can be a bit more relaxed about the weather ;-)  Steel and outdoors are not always the best of buddies, and if the floor is earth then maybe you do not want a big chunk of TNCs earth exposed ?

    Mike.

  • I

    Some pictures above, you can see the meter cabinet under the log store roof. It's a balance between shock risk and fire risk. 

    Also thinking things through I may leave the solar/ battery guys to install an extra meter box etc as the customer wants the battery to work in island mode and they are going to have to figure out how to disconnect the garage loads when in island mode. 

Reply
  • I

    Some pictures above, you can see the meter cabinet under the log store roof. It's a balance between shock risk and fire risk. 

    Also thinking things through I may leave the solar/ battery guys to install an extra meter box etc as the customer wants the battery to work in island mode and they are going to have to figure out how to disconnect the garage loads when in island mode. 