Does a 50m extension lead need to be fitted with an RCD?

I have completed C&G 2377-77 EET / PAT TESTING COURSE and am now seeking some clarification on the code of practice.

In the CoP in section 10.10 gives recommended maximum lengths for extension leads, but these can be exceeded if an RCD is fitted.

My question is, if I have a 50m extension to test, should I be failing it if it is not fitted with an RCD?

If it should have one fitted, why are retailers allowed to sell them without?

Parents
  • Can I take it that the RCD will be fitted at the supply end of these cables with fault protection rather than additional protection in mind?

  • Can I take it that the RCD will be fitted at the supply end of these cables with fault protection rather than additional protection in mind?

    Who knows? Neither BS EN 61242 nor BS EN IEC 61316 let us in on that secret (in fact, they don't specify an RCD as per above ... but they might ... but no guarantee ... be based on the assumption that BS 761 generally requires additional protection for socket-outlets rated up to 32 A in the general case)

    Nor are we looking at requirements of BS 7671 alone, which effective (bar additional protection) cease at the socket-outlet.

    However, a fair bet all things being even.

Reply
  • Can I take it that the RCD will be fitted at the supply end of these cables with fault protection rather than additional protection in mind?

    Who knows? Neither BS EN 61242 nor BS EN IEC 61316 let us in on that secret (in fact, they don't specify an RCD as per above ... but they might ... but no guarantee ... be based on the assumption that BS 761 generally requires additional protection for socket-outlets rated up to 32 A in the general case)

    Nor are we looking at requirements of BS 7671 alone, which effective (bar additional protection) cease at the socket-outlet.

    However, a fair bet all things being even.