Domestic Power Wiring - Upstairs & Downstairs

I have surveyed a house and have observed a domestic ring circuit which is serves a floor area exceeding 100m2, including upstairs, downstairs and utility containing (washing machine and tumble dryer) (kitchen ring is separate). I am ok with this circuit contravening the 100m2 guidance, and not being respective to the load of the whitegoods, but I understand there is guidance on a domestic ring only covering a single level.

Can somebody point me towards this guidance either in published Guidance Notes or the Regulations.

Thanks

Slight smile

Parents
  • The Question is:

    I have surveyed a house and have observed a domestic ring circuit which is serves a floor area exceeding 100m2, including upstairs, downstairs and utility containing (washing machine and tumble dryer) (kitchen ring is separate). I am ok with this circuit contravening the 100m2 guidance, and not being respective to the load of the whitegoods, but I understand there is guidance on a domestic ring only covering a single level.

    Can somebody point me towards this guidance either in published Guidance Notes or the Regulations (ie IET, NICEIC, NAPIT ect).

    Thanks

  • Probably not - because I'm quite confident that in the IET guidance notes and the Regs, such unnecessarily  restrictive advice does not exist.

    Less confident about NIC/NAPIT et al -  they say some odd things at times and they may have.

    M.

Reply
  • Probably not - because I'm quite confident that in the IET guidance notes and the Regs, such unnecessarily  restrictive advice does not exist.

    Less confident about NIC/NAPIT et al -  they say some odd things at times and they may have.

    M.

Children
  • Probably not - because I'm quite confident that in the IET guidance notes and the Regs, such unnecessarily  restrictive advice does not exist.

    I agree with Mike.

    What, for example would you do with a mezzanine level? If circuits in general were limited to a single floor, you could never have 2-way lighting up a stairs.