Permissible inrush current single phase

Hi

I have had the misfortune to buy a Lincat Combination Oven for my Hotel.

These normally come in 10kw three phase.  3 x  13amps That's not too bad.

I have the single phase version 1 x 39 amps. Not so good.

It is operating at 1 second on 39 amps

                          0.2 second off  0 amps

                          Cycling continually. for hours.

I have a 40kva single phase supply and can hear the current hammering away incessantly. Lights flickering etc. I asked the manufacture for details of soft starting and duty cycle. They say this is the way they were designed to work. Bang on and Bang off --1 second cycle continually.

I don't have a current (Hee Hee)  Reg book. So I ask is there a reg in place that covers the single phase load criteria.

To add insult to injury-- I have a three phase 65kva standby set.-- I would not put that destructive abuse on one of my 20kva phases, it would shake it apart. So I cannot run it.

Regards -- Tony

Parents
  • All of these depend on the applied motor (or whatever) being linear with the control signal, on-off is not.

    I think a lot of systems these days achieve an approximation of linear control with hard-on-off switching pulses and then something to smooth the results. Many inverters simply have a fixed d.c. line and switch that on or off at varying speeds/ratios to generate the output - at best a totem pole arrangement between a +ve and -ve d.c. rail - so at that point only two (or three) single voltages can be produced +dc & 0 (or +dc, 0 and -dc). It then relies on smoothing to produce an approximation to the a.c. waveform output expected - occasional narrow pulses yielding a smoothed voltage near to zero, more frequent and/or wider pulses to produce the peaks of the a.c. output. I reckon the oven is working on the same principle - just using thermal inertia rather than inductor or capacitors to do the smoothing. A 1s or 2s switching period is probably quite reasonable from a thermal point of view (if not a single phase supply point of view).

       - Andy.

Reply
  • All of these depend on the applied motor (or whatever) being linear with the control signal, on-off is not.

    I think a lot of systems these days achieve an approximation of linear control with hard-on-off switching pulses and then something to smooth the results. Many inverters simply have a fixed d.c. line and switch that on or off at varying speeds/ratios to generate the output - at best a totem pole arrangement between a +ve and -ve d.c. rail - so at that point only two (or three) single voltages can be produced +dc & 0 (or +dc, 0 and -dc). It then relies on smoothing to produce an approximation to the a.c. waveform output expected - occasional narrow pulses yielding a smoothed voltage near to zero, more frequent and/or wider pulses to produce the peaks of the a.c. output. I reckon the oven is working on the same principle - just using thermal inertia rather than inductor or capacitors to do the smoothing. A 1s or 2s switching period is probably quite reasonable from a thermal point of view (if not a single phase supply point of view).

       - Andy.

Children
No Data