Reg 419.2 Applicable to VSD driven motor?

Good afternoon,

When using cable design software such as ElectricalOM, there is a check box within the "Earthing" tab / adiabatic check of CPC. It states Provision of  regs 419.2 & 419.3 are applicable. (BS7671)

If checked it will remove the warning regarding the earth fault / disconnection time (should a warning exist with the modelled install)

Can someone confirm with a degree of certainty that the checkbox would reg 419.2 be applicable to a motor supplied from a VSD drive? 

Parents
  • Can you give an example of where 419.2 is applicable then please? i.e where power electronic converters are part of the fixed installation? I am struggling to think of another.

    UPS systems? Inverter generators?

       - Andy.

Reply
  • Can you give an example of where 419.2 is applicable then please? i.e where power electronic converters are part of the fixed installation? I am struggling to think of another.

    UPS systems? Inverter generators?

       - Andy.

Children
  • Ah yes. UPS, perfect example. So why would you consider a UPS part of fixed install and not VSD inverter?