Can 3 individual mcbs(instead of a 3 or 4 pole mcb) be used for circuit protection of a 3 phase distribution circuit, where a 4 or 5 core swa is used? Is there a requirement that all phases must be disconnected in the event of a fault?
Can 3 individual mcbs(instead of a 3 or 4 pole mcb) be used for circuit protection of a 3 phase distribution circuit, where a 4 or 5 core swa is used? Is there a requirement that all phases must be disconnected in the event of a fault?
It would effectively be 3 single phase circuits sharing a neutral. Which brings to mind neutral currents. If for example, three single phase 40A circuits sharing a neutral of a 10mm SWA would result in 120A neutral currents.. too much
But how is it ok for meter tails to be the same size on 3 phase supplies?
Yes if they were all on the same phase; no if they are different phases.
Ah yes of course.
Need to brush up on my 3 phase theory!
Ah yes of course.
Need to brush up on my 3 phase theory!