Adding spurs to immersion heater circuit

About 25 years ago we had a shower fitted and the plumber added a fused spur to the immersion heater circuit for the pump.

I want to upgrade our heating system by fitting an ebus controller in the airing cupboard. This needs a mains supply and there is no accessible ring circuit. Is it permissible to add another fused spur to the immersion circuit?

Mike

Parents
  • Strictly speaking this is not a "spur", simply part of a radial circuit, which like a tree, may have many branches. Anyway not a problem at 2VA!

Reply
  • Strictly speaking this is not a "spur", simply part of a radial circuit, which like a tree, may have many branches. Anyway not a problem at 2VA!