Exported PME to steel floodlight columns, public tennis courts

Hi

We're doing an EICR at a local tennis club. It has a number of  3 phase floodlights mounted on galavanised columns illuminatimg outdoor tennis courts.

They are earthed via an exported PME TNCS system which was surprising because we'd imagined they would have sunk an earth rod at each column and not exported the PME.

The location is open to the public. Circuits not 30mA RCD protected foir additional protection.

I'm no

Many Thanks for your help

Parents
  • Section 714

    Outdoor lighting installations

    714.411.3.4 Additional protection 

    Lighting that is accessible to the public shall have additional protection by an RCD having the characteristics specified in Regulation 415.1.1.

    My understanding is the impetus behind the introduction of this regulation, in amongst others, was the incident in a pub garden resulting in the death of a child.

    www.bbc.co.uk/.../uk-england-london-56758749

Reply
  • Section 714

    Outdoor lighting installations

    714.411.3.4 Additional protection 

    Lighting that is accessible to the public shall have additional protection by an RCD having the characteristics specified in Regulation 415.1.1.

    My understanding is the impetus behind the introduction of this regulation, in amongst others, was the incident in a pub garden resulting in the death of a child.

    www.bbc.co.uk/.../uk-england-london-56758749