Exported PME to steel floodlight columns, public tennis courts

Hi

We're doing an EICR at a local tennis club. It has a number of  3 phase floodlights mounted on galavanised columns illuminatimg outdoor tennis courts.

They are earthed via an exported PME TNCS system which was surprising because we'd imagined they would have sunk an earth rod at each column and not exported the PME.

The location is open to the public. Circuits not 30mA RCD protected foir additional protection.

I'm no

Many Thanks for your help

Parents
  • There is nothing to say that the RCD requirement depends on the height of the light source

    But it is dependent on the light being "accessible to the public" - my point is that if it's umpteen metres up in the air, it's not accessible to the public.

       - Andy.

Reply
  • There is nothing to say that the RCD requirement depends on the height of the light source

    But it is dependent on the light being "accessible to the public" - my point is that if it's umpteen metres up in the air, it's not accessible to the public.

       - Andy.