Exported PME to steel floodlight columns, public tennis courts

Hi

We're doing an EICR at a local tennis club. It has a number of  3 phase floodlights mounted on galavanised columns illuminatimg outdoor tennis courts.

They are earthed via an exported PME TNCS system which was surprising because we'd imagined they would have sunk an earth rod at each column and not exported the PME.

The location is open to the public. Circuits not 30mA RCD protected foir additional protection.

I'm no

Many Thanks for your help

Parents
  • The Regulation 714.411.3.3 in the 18th Edition has been expanded and become 714.411.3.4 in the 18th Edition Amendment Two, broadening the requirement for 30 mA RCD protection to include gardens, spaces open to the public.

  • Yes, I would agree with you Sparkingchip. Strict reading of the regulation would require 30mA RCD protection for the tennis court lighting. After all they are in a space open to the public. Not sure if that was the intention but that’s neither here or there. 

Reply
  • Yes, I would agree with you Sparkingchip. Strict reading of the regulation would require 30mA RCD protection for the tennis court lighting. After all they are in a space open to the public. Not sure if that was the intention but that’s neither here or there. 