Exported PME to steel floodlight columns, public tennis courts

Hi

We're doing an EICR at a local tennis club. It has a number of  3 phase floodlights mounted on galavanised columns illuminatimg outdoor tennis courts.

They are earthed via an exported PME TNCS system which was surprising because we'd imagined they would have sunk an earth rod at each column and not exported the PME.

The location is open to the public. Circuits not 30mA RCD protected foir additional protection.

I'm no

Many Thanks for your help

Parents
  • 714.411.3.4 has made its way onto the NAPIT domestic installations EICR Schedule of Inspections, so I have already found myself questioning it’s scope.

    engx.theiet.org/.../129635

  • Hmmm  that is strange as it's  already covered in 411.3.4 and domestic fall outside anything listed in 714.411.3.4

Reply
  • Hmmm  that is strange as it's  already covered in 411.3.4 and domestic fall outside anything listed in 714.411.3.4