Exported PME to steel floodlight columns, public tennis courts

Hi

We're doing an EICR at a local tennis club. It has a number of  3 phase floodlights mounted on galavanised columns illuminatimg outdoor tennis courts.

They are earthed via an exported PME TNCS system which was surprising because we'd imagined they would have sunk an earth rod at each column and not exported the PME.

The location is open to the public. Circuits not 30mA RCD protected foir additional protection.

I'm no

Many Thanks for your help

Parents
  • For interest only, I just had a peep at 714 in the Irish Regs, also founded on 60364. 30mA RCD protection is not required for luminaires mounted at a height of +2.8m. Like 7671, the term luminaire does not include the column. Also, in common with 7671 IPXXB or IP2X is required with the enclosure open. So, I would agree with Patrick that the rather poor design of the arrangement inside the column that he describes warrants a code 2. I have seen too many of this type of enclosure either defective or missing to have anything less.

Reply
  • For interest only, I just had a peep at 714 in the Irish Regs, also founded on 60364. 30mA RCD protection is not required for luminaires mounted at a height of +2.8m. Like 7671, the term luminaire does not include the column. Also, in common with 7671 IPXXB or IP2X is required with the enclosure open. So, I would agree with Patrick that the rather poor design of the arrangement inside the column that he describes warrants a code 2. I have seen too many of this type of enclosure either defective or missing to have anything less.