TT earthing system - external earth loop impedance (Ze), Ze on test certificate and earth resistance Ra

We have a TT earthing system for a 3-phase + N 400V system. Could anyone please help me with the questions below? 

We will need to measure the earth electrode resistance in order to use equation Ra x In < 50V. As per BS 7671 Guidance Note 3 method 2, we are allowed to use "a loop impedance tester" to "connect between the line conductor at the source of the TT installation and the earth electrode, and a test performed." Then impedance reading taken is treated as the electrode resistance. We use this value for "Resistance to earth" on the test certificate. 

Question 1: Is this measured value actually the external earth loop impedance  (Ze) for a TT earthing system? So does this mean that TT earthing system Ze includes Ra (earth resistance of the electrodes) i.e. Ra is part of Ze of a TT earthing system? Or Ze is still the external components (supply cable, transformer neutral etc.) without the Ra, and the tested value is Ze + Ra? This is not quite clear to me. All calculations refer to Zs = Ze + (R1+R2), in terms of TT earthing system, should Ze already include Ra? 

For the "Nature of Supply Parameters" section of a test certificate, we use the BS 7671 recommended method to measure the 3-ph prospective short circuit current. There is a Ze we need to fill in this section. 

Question 2: For the Ze in this "Nature of Supply parameters" section of the test certificate, should we use the reading from method 2 of of Guidance note 3 mentioned above? i.e. the reading which includes the Ra value as well. 

These two questions are related. Maybe the external component impedance are relatively small compared with the Ra and we assume Ra = Ze? 

Please help.

Many thanks 

Parents
  • The usual conventions are a little muddled - by the definitions, the customer's electrode is part of the consumer's installation, so is not external to it, so Ze does NOT include Ra (although it would, for TT, include the supplier's electrode(s) - Rb).  Hence you get things like statements like the max Ze for TT systems is 21Ω yet Ra can often be in the region of 200Ω.

    Really things like Zs = Ze + R1+R2 should only be done for TN systems, originally the requirement for TT systems didn't depend on the loop impedance, just Ra (which technically actually included R2 already).

    The point about using a loop meter is that it includes all of Ra ... plus extra bits for the supplier. As the supplier's bit are never going to provide a -ve impedance, if the loop meter gives you an acceptable number, you can be sure that Ra will be less than that - so always compliant. So is a quick, easy but still clean, method of showing compliance. The downside is that if the loop meter shows a value that's just a little too high, you can't then tell if it complies or not - the extra bit could be down to the supplier's side in which case Ra would be OK, or it might be down to Ra in which case it would be a fail - but you can't really tell using a test meter - so either just assume the worst or get hold of a more expensive instrument. In the real world though, electrodes buried in the ground are quite variable beasts - actual resistance figures varying considerably with the weather and season so any practical design and installation will have to include very substantial safety margins anyway - so the difference between loop figures and Ra are usually smaller than would be significant anyway.

                - Andy.

  • Thank you Andy. In this case of TT earthing system, is it still necessary to add a "Ze" value on the test certificate if it is not really known unless we could deduct the actual Ra from the loop measurement? Basically we only need to assess In x Ra < 50V. Should we just write down "max 21ohm" or just "n/a" for the Ze? I have also seen people using the loop test results (external impedance + Ra) for the Ze value on the test certificates, which is not correct based on your explanation above. many thanks 

Reply
  • Thank you Andy. In this case of TT earthing system, is it still necessary to add a "Ze" value on the test certificate if it is not really known unless we could deduct the actual Ra from the loop measurement? Basically we only need to assess In x Ra < 50V. Should we just write down "max 21ohm" or just "n/a" for the Ze? I have also seen people using the loop test results (external impedance + Ra) for the Ze value on the test certificates, which is not correct based on your explanation above. many thanks 

Children
  • Thank you Andy. In this case of TT earthing system, is it still necessary to add a "Ze" value on the test certificate if it is not really known unless we could deduct the actual Ra from the loop measurement? Basically we only need to assess In x Ra < 50V.

    Where RCDs are used for fault protection, compliance with Regulation 411.5.3 is demonstrated by earth fault loop impedance Zs being less than the values in Table 41.5. Similarly, if an OCPD is used for ADS in TT systems, Note 1 to Regulation 411.5.2 tells us to assess Zs. So I would argue that earth fault loop impedance Zs is what's verified (assessed) in TT systems, as required by BS 7671, and we do NOT directly verify (assess) either IΔn×RA<50 V or In×RA<50 V.

    I agree that strictly Ze for a TT system does not include the consumer's earth electrode resistance REE, because the electrode is part of the installation, and the table of Symbols in Part 2 tells us that Ze is external to the installation.But that doesn't make Ze less important to the installation, and verifying (Ze+RA)

    However, for verification, as discussed above we have to verify Zs (where RCDs are used for ADS, this is required to be less than the values in Table 41.5). Hence, if Ze is measured to include REE, the formula Zs=Ze+(R1+R2) could still be used rather than measuring Zs directly. (Noting that, for armoured cables, for  the measured values would need modifying by the relevant formula from PD IEC/TR 50480 to get the value of (R1+R2) to use, see Guidance Note 6 and OSG ... and also noting that the armour needs a different temperature correction factor to copper conductors in SWA).

    If you wanted to be more factual regarding the measured value, why not record '(Includes REE)' next to the value of Ze recorded on the certificate?

  • Hi Graham thank you for your explanation. It is now clear to me. We will need to meet both 411.5.3 (i) and (ii). For a site with earth leakage protection, 411.5.3 (i) is very easy to meet even considering the worst Ze (as high as 21 ohms, thus conservative Zs). We will also use Ra (measured from the loop tester -> Ze + Ra) to assess if we meet 411.5.3 (ii). We will put down the measured Ze+Ra against Ze on the certificate and note down that it includes Ra. 

  •   , RA is the sum of (REE+R2) in this case -  If you wanted to measure RA, you'd have to include R2 to the exposed-conductive-parts (because  for 411.5.3, RA includes that resistance).

    and therefore you would be:

    • measuring (Ze+REE) at the origin (and recording the value for Ze includes REE) - see Note to 643.7.1 b) (1); and
    • measuring or determining Zs by other means at the extremity of each circuit to comply with either:
      • Table 41.5 where RCDs are used for ADS (see Regulation 411.5.3 and NOTE to 643.7.1); or
      • the formula Zs ≤ U0×Cmin÷Ia  where OCPDs are used (see Regulation 411.5.4, Ia being the value of current causing operation of an OCPD according to the disconnection time of Regulation 411.3.2.2 or 411.3.2.4, usually 0.2 s or 1 s depending on circuit rating/function for 230/400 V TT supplies, although for installations within buildings where protective bonding is in place, disconnection times for TN systems may be used for circuits covered by Regulation 411.3.2.2)

    Interesting, though, that, having discussed the designer's obligations, where RCDs are used for ADS, the person carrying out initial/periodic verification also needs to verify the effectiveness of protection by testing the RCD as well as verifying that the requirements of Chapter 41 are met (see Regulation 643.7.1 b) (2) and related NOTE). Having said that, this is the minimum standard.

    Note: we ought to be careful, Ra is defined differently to RA as well - see Page 47 of BS 7671:2018+A2:2022

  • Graham, thank you for your help.