Hi, 

I am looking at using an electronic relay with 1 single phase input and 4 switched outputs.

Each output can be loaded to a max. 16A with a device maximum of 40A. This means the relay itself (its input) would need to be protected by a 40A breaker. The input is split between 4 outputs internally. 

The question I have is regarding the outputs. Obviously 16A on a 2.5mm cable is fine in most circumstances, however would a 40A MCB suffice for short circuit protection, if the loads connected to the relay are known (e.g. electrical heaters, pulling say 13A). The fixed load would ensure protection against overload, but would the above provide adequate short circuit protection? 

Would I be better installing additional MCBs on the relay outputs, even if all loads are known/fixed? 

Thanks. 

Parents
  • Please understand I'm not a panel design expert -

    Perhaps use those 4 outputs to switch 4 small contactors (Which have their own circuits running through them) or use a single N/O or N/C relay to switch a 4 pole contactor with 4 circuits on it. 

    If you had to do it the way you've described, I'd see no harm at all in adding circuit protection for those downstream "Circuits", you'd have to be careful with the neutrals though, because those loads would also add up. I'm no theoretical expert on controls, but having worked with controls a bit, it's Definitely not what I'd expect to find or see, so it might create future problems when someone like me comes to fault find or perhaps even pass the new installation. 

    Are you responsible for the design?

Reply
  • Please understand I'm not a panel design expert -

    Perhaps use those 4 outputs to switch 4 small contactors (Which have their own circuits running through them) or use a single N/O or N/C relay to switch a 4 pole contactor with 4 circuits on it. 

    If you had to do it the way you've described, I'd see no harm at all in adding circuit protection for those downstream "Circuits", you'd have to be careful with the neutrals though, because those loads would also add up. I'm no theoretical expert on controls, but having worked with controls a bit, it's Definitely not what I'd expect to find or see, so it might create future problems when someone like me comes to fault find or perhaps even pass the new installation. 

    Are you responsible for the design?

Children
  • Hi,

    Switching contactors is one option however the relays are rated at 16A so they can be used to switch the load directly. The manufacturer states acceptable load types (resistive, inductive, capacitive). 

    Thanks. 

  • The 2.5mm cable will be OK to trip a 40A B type on all but the longest circuit, assuming  the voltage drops at 16A are 5% or less.
    If it is sensible to fuse or MCCB the loads ? that  is an interesting one. Personally I'd consider it wise, as if not one maybe has to consider odd faults like heater elements shorting to ground half way along. 13A fuses are cheap ;-)

    Also be aware that relays have a far shorter life at full load than lightly loaded, and it depends how it will be used - a load tripping on and off every few seconds for a week is a lot worse than switching on and off once a day for a decade. Can the relays be changed or is it a whole module job? You may need suppressors at the contacts as well.

    M