Tackling AFDD Tripping

How are people tacking AFDD tripping?

In the past if I had a call out for a tripping RCD/RCBO or MCB there are well established procedures and tools to track down the fault.

These range from the visual inspection, insulation resistance testing, earth leakage measurement, RCD ramp testing and RCD time testing. It would not take too long to track down the fault whether it was faulty appliance, water ingress, damaged cable or even a duff protective device. The repair might have taken a bit longer but at least you knew where the fault was.

I had a call out this weekend for a AFDD that was tripping on a ring circuit. The new consumer unit (with 3- AFDDs, RCBOS and surge protection) has been in service the end of November and no issues reported. The customer did his own diagnosing and suspected the fridge/freezer as the circuit stopped tripping when he removed the appliance from the circuit. However, when he plugged the fridge/freezer in to another ring circuit with AFDD protection via a extension lead on a reel it did not trip. At this point I did not know what type of fault it was as the customer did not make a note of LED status on the AFDD.

The fridge has no damage and continuity and insulation resting testing all OK

Ring circuit was intact and insulation testing OK (greater than 500Mohm). The instrument readings were exactly the same as they were at the end of November. Plugged it back in and no tripping. I also ran a 1.8kW load on the same socket for a few minutes to see if I could get it to trip -  all OK.

Ten minutes after leaving the circuit tripped, I returned and from the flashing light sequence on the AFDD it was definitely an ARC fault. Reset the breaker and is was tripping regularly every few minutes.

I plugged in the fridge into another circuit, but this time with my much shorter extension lead. Then proceeded to inspect all sockets and checking tightness of terminals - no issues. Although there are some terminations not accessible for inspection.

Then I noticed the other circuit tripped (with fridge connected via extension lead) - so the conclusion that it is definitely the fridge. As the fridge/freezer is still under warrantee I advised the customer to contact the manufacturer. He plugged it into the original circuit in the hope to keep it running. It did not and I told him again to not run the fridge.

Later that night I get a message that now the other circuit is tripping every time they use the microwave -  not the circuit with the fridge and apparently fridge not plugged in.

At the moment I am not 100% sure it is the fridge and can't rule out a faulty AFDD or has the faulty fridge caused the  microprocessor in the AFDD to go faulty.

As a last resort I told them to switch off all circuits and main-switch and then switch-on one by one. Thinking that these devices have microprocessors maybe they need a restart every now and again - bit like my router at home.

Any suggestions on diagnosing ARC faults?

Parents
  • Just wondering.

    Are AFDD's double pole or do they have some element of a shared neutral and could a fault on the neutral of one circuit trigger the AFDD on another circuit. Also would a fault up stream of the AFDD cause the AFDD to trigger.

  • 1P+N are switched, so double pole

  • Part of the problem is that in the absence of either a proper recognized AFDD tester or proper published data about the internals, is that we really know neither what it should do, nor how to tell if it is doing it or not. It may be that the fridge really is arcing internally, or it may just have a rather inadequate suppressor on the thermostat contacts.

    Or the AFDD may be over sensitive. To that end probably carrying around some plug in low pass filtering may also be a useful diagnostic as well as a line scope and perhaps a test pulse injector all of which rapidly becomes  utterly unreasonable in the context of a 'fix my trip' call out.

    Mike

  • If you have tested the wiring again as you mentioned above, then this should rule out any problem with the neutral unless the device itself is faulty.

    Ring Finals offer up a few pitfalls for AFDDs, so testing the neutrals is important.

    Neutrals are a good place to start though, plus, there have also been some instances of 'sympathetic tripping' with these devices when a AFDD trips on an adjacent circuit next to the problematic one, this phenomena is apparently not unusual and can lead to many happy hours of false trails when fault finding.

Reply
  • If you have tested the wiring again as you mentioned above, then this should rule out any problem with the neutral unless the device itself is faulty.

    Ring Finals offer up a few pitfalls for AFDDs, so testing the neutrals is important.

    Neutrals are a good place to start though, plus, there have also been some instances of 'sympathetic tripping' with these devices when a AFDD trips on an adjacent circuit next to the problematic one, this phenomena is apparently not unusual and can lead to many happy hours of false trails when fault finding.

Children
No Data