RBCO trips when I switch off circuit, can only reset by closing light switch, circuit has been working normally, suspect condensation but still odd
RBCO trips when I switch off circuit, can only reset by closing light switch, circuit has been working normally, suspect condensation but still odd
That sort of voltage is perfectly possible due to capacitive coupling, especially with 2-way lighting. What current flows when the circuit is off? (Use fused probes.)
That sort of voltage is perfectly possible due to capacitive coupling, especially with 2-way lighting. What current flows when the circuit is off? (Use fused probes.)
Thanks Chris, I suspected that may be a reason, why would the RCBO trip when power removed from circuit
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site