RBCO trips when I switch off circuit, can only reset by closing light switch, circuit has been working normally, suspect condensation but still odd
RBCO trips when I switch off circuit, can only reset by closing light switch, circuit has been working normally, suspect condensation but still odd
Is the polarity correct throughout? If the switch was in the N for instance opening the switch would mean that the wiring between the switch and lamp would be held at 230-ish volts - whereas it would be close to zero (neutral potential) with the switch closed. A high impedance fault to earth on that wiring (e.g. due to condensation or corrosion) would then leak more current to earth while the switch was open - which could be the cause of the RCD tripping.
- Andy.
Is the polarity correct throughout? If the switch was in the N for instance opening the switch would mean that the wiring between the switch and lamp would be held at 230-ish volts - whereas it would be close to zero (neutral potential) with the switch closed. A high impedance fault to earth on that wiring (e.g. due to condensation or corrosion) would then leak more current to earth while the switch was open - which could be the cause of the RCD tripping.
- Andy.