Coding for Sockets Following EICR

Gents/Ladies, We have just had an EICR carried out on our premises (industrial) and the following Code C3 as been given for no RCD protection on sockets. I was under the impression that all single phase and three phase sockets up to 32amp were required to have RCD'S/RCBO'S or RCD sockets, unless a written Risk Assessment was issued. Is this correct?

Parents
  • I was under the impression that all single phase and three phase sockets up to 32amp were required to have RCD'S/RCBO'S or RCD sockets, unless a written Risk Assessment was issued. Is this correct?

    It is not clear what you have in mind if that were the case; or not.

    What do you think the inspector should have done?

Reply
  • I was under the impression that all single phase and three phase sockets up to 32amp were required to have RCD'S/RCBO'S or RCD sockets, unless a written Risk Assessment was issued. Is this correct?

    It is not clear what you have in mind if that were the case; or not.

    What do you think the inspector should have done?