House supply TT and loadings

Is there a limit to what an overhead supply can handle, loading wise?

Sorry if that sounds daft, I haven't worked with TT much in the past.

Existing house has an oven supply, no electric shower, and just your average size place with normal amount of circuits for a 3 bedroom house.

Fuse is 60/80A

A double garage is being built for a car enthusiast, he is requesting the following.

An electric garage door. ( no details as of yet )

Car Stacker Lift ( no details as of yet )

2 HP compressor

AC unit ( external condenser with one cassette inside ) ( around 4 amps )

General sockets and LED lighting.

Submain length is 45 meters.

My initial thoughts was to install a 10mm 2 core to a new DB which will be staked  SPD and RCBO's 

I can't see that the equipment will be used at the same time, at the most maybe the AC will be on while he is lifting a car in the air with a few general things plugged in and the lights on.

Compressor won't be used at the same time the door is being opened or a car is being lifted in the air for example.

I thought the 10mm will be ok on a 32A MCB protected by the 100ma main switch.

Now is is asking for a car charger. I have suggested a Zappy which is 7kw

So now I'm thinking of a 16mm 2 core on a 40A MCB

Your thoughts would be apreciated.

Parents
  • Relatively small and short term loads such as power operated garage doors or vehicle lifts can generally be ignored when considering if the incoming supply is sufficient.

    An air compressor is more of a concern due to inrush or starting currents resulting in lamp flicker. A small air conditioing unit is unlikely to much matter as will be used only in hot weather when electric space heating is not used.

    A 7kw EV charger is more of a concern as it is a long hour load. I would be very doubtful about a 7kw charger on a service of less than 100 amps.

Reply
  • Relatively small and short term loads such as power operated garage doors or vehicle lifts can generally be ignored when considering if the incoming supply is sufficient.

    An air compressor is more of a concern due to inrush or starting currents resulting in lamp flicker. A small air conditioing unit is unlikely to much matter as will be used only in hot weather when electric space heating is not used.

    A 7kw EV charger is more of a concern as it is a long hour load. I would be very doubtful about a 7kw charger on a service of less than 100 amps.