Disconnection times on a system if a stand by generator is used

On a fully designed power distribution system, clearly the fault levels, earth loop impedances and ultimately fuse disconnection times are determined by the system parameters Transformer %Z etc one or two in parallel for min and max fault levels levels. What needs to be considered when bringing on a stand-by generator, clearly all Fault levels, Earth loop impedances and consequently fuse disconnection times would change because of the Generator parameters. How would you design in these new parameters, bearing in mind that disconnection times on a large system may no longer be achievable 

Parents
  • Taking up on some earlier comments, using RCD as a solution, raises a few other issues I.e. by doing so you are making the system, particular when maintaining essential supplies less secure.

    as an example on one project, a UPS was used to maintain lighting on mains failure. The lighting design had a number of distribution boards housing 5amp fuses for final sub-circuits. the UPS manufacturer was asked to prove that during FAT, under an fault condition would the 5amp fuse disconnect, L-N and Zs impedances for the circuits were given for simulation, they could not provide evidence.

    i guess has anyone got any empirical evidence on how these issues were overcome.

  • as an example on one project, a UPS was used to maintain lighting on mains failure. The lighting design had a number of distribution boards housing 5amp fuses for final sub-circuits. the UPS manufacturer was asked to prove that during FAT, under an fault condition would the 5amp fuse disconnect, L-N and Zs impedances for the circuits were given for simulation, they could not provide evidence.

    This is a supply to safety services, and should comply with the relevant standards. It's a specific case. See Regulation 560.5.3, which leads to a design decision to perhaps consider IT system for those circuits? Where BS 7671 applies to this type of installation, Regulation 560.7.4 effectively tells us to provide an appropriate number of circuits so that OCPD operation does not impair other circuits.

    BUT

    See earlier post - this isn't simply a UPS, but a CPS - and the requirements of BS EN 50171 and Regulation 560.6.10 of BS 7671 apply to the "UPS" itself - but the whole system ought to comply with the BS 5266 and BS EN 1838.

Reply
  • as an example on one project, a UPS was used to maintain lighting on mains failure. The lighting design had a number of distribution boards housing 5amp fuses for final sub-circuits. the UPS manufacturer was asked to prove that during FAT, under an fault condition would the 5amp fuse disconnect, L-N and Zs impedances for the circuits were given for simulation, they could not provide evidence.

    This is a supply to safety services, and should comply with the relevant standards. It's a specific case. See Regulation 560.5.3, which leads to a design decision to perhaps consider IT system for those circuits? Where BS 7671 applies to this type of installation, Regulation 560.7.4 effectively tells us to provide an appropriate number of circuits so that OCPD operation does not impair other circuits.

    BUT

    See earlier post - this isn't simply a UPS, but a CPS - and the requirements of BS EN 50171 and Regulation 560.6.10 of BS 7671 apply to the "UPS" itself - but the whole system ought to comply with the BS 5266 and BS EN 1838.