3 PHASE KMF SWA

I am looking for a product to provide over current protection  for a 12m run of meter tails/swa from the meter cabinet to the distribution board. The problem I am having is its a 3 phase domestic supply likely to be run in SWA. Also will this be permitted to be fixed in the meter cabinet?  

Parents
  • I think that you would struggle to find a TP(S)N switch-fuse which would be small enough to fit in a single meter cabinet with the usual tackle.

    FWIW, we have a switch-fuse in a separate box next to the meter box. No reason why they should not be one above the other except that in our case there is a window above. The SWA runs under the adjacent room and then up the wall beyond, so a little less than 12 m. For some reason, 5 core cable has been used. Installed circa 1982, but not for much longer.

    The tails between the boxes are enclosed by a short length of conduit.

Reply
  • I think that you would struggle to find a TP(S)N switch-fuse which would be small enough to fit in a single meter cabinet with the usual tackle.

    FWIW, we have a switch-fuse in a separate box next to the meter box. No reason why they should not be one above the other except that in our case there is a window above. The SWA runs under the adjacent room and then up the wall beyond, so a little less than 12 m. For some reason, 5 core cable has been used. Installed circa 1982, but not for much longer.

    The tails between the boxes are enclosed by a short length of conduit.