18th edition question

  hi started to study for my 18th, wots you guys think the answer is, something tells me it’s different to wots on the answer sheet 

Parents
  • Bonding is generally reserved to describe connexions things that are not part of the circuit primary ADS path, so the ones to the tap and the gas meter, This Q refers to is a main CPC if you like.  In the common vernacular the main earth wire.

    MET is often said to be where bonds and CPCs meet, but that is often inside the CU, rather than at a marshaling block as here.

    M.

Reply
  • Bonding is generally reserved to describe connexions things that are not part of the circuit primary ADS path, so the ones to the tap and the gas meter, This Q refers to is a main CPC if you like.  In the common vernacular the main earth wire.

    MET is often said to be where bonds and CPCs meet, but that is often inside the CU, rather than at a marshaling block as here.

    M.