RCD Risk Assessment Permitted Exception

I posted the same question to Reddit, plus here in the hope I can find someone with the knowledge/template.

Reddit post link for those who wish to reply there - https://www.reddit.com/r/ukelectricians/comments/10yu2hy/rcd_risk_assessment_permitted_exception/

I've copied the question below for those who prefer to reply here; thanks in advance!

Does anyone have a risk assessment example or template to support measures that would help with the permitted exception of RCDs in BS 7671, 411.3.3?

The use case is an industrial environment where skilled persons connect equipment/machinery for testing/commissioning purposes. There are two IEC 60309 (CEEFORM) outlets, one 63A and one 125A; 400 V 3P+N+E 6h.

Note - on the same site, there is a custom third-party distribution panel with 100mA RCD protection and a key switch capable of bypassing the RCD altogether (keys held by authorised persons). The company wants a similar arrangement in a new part of their building, hence the need for a risk assessment.

Edit - this is common practice in the related industry; up to 50+ VFDs can be connected to these circuits, which generate leak current via the filters.

Any feedback or support is welcomed!

Parents
  • 411.3.3 only applies to sockets not exceeding 32 A so you do not need a DRA to comply. That said, risk assessments are always sensible in a working environment because of the duty of care which an employer owes to his employees.

Reply
  • 411.3.3 only applies to sockets not exceeding 32 A so you do not need a DRA to comply. That said, risk assessments are always sensible in a working environment because of the duty of care which an employer owes to his employees.