Thoughts on running cables behind aga

I am putting wiring in to a grade 2 listed building for a new kitchen.

I need to get 3 circuits past an aga to a kitchen island. I can't disturb the original flagstone flooring.

Sockets, 1 double and one socket socket at counter height, end of radial circuit

13 amp oven (based on manufacturers recommendation)

20 amp induction hob (based on manufacturers recommendations, has option to reduce.)

I could go in front of the aga as it's slightly raised but it's going to look unsightly and could actually be warmer than the back.

The aga is in a very large open fire place and I could drill through the side of the fireplace to run cables at the back, the back seems quite cool, especially at the bottom, I need to measure but would guess about 30 deg C.

Some numbers below

What do you think about the overall concept, do you have any experience with aga's, is it reasonable to assume the rear temperature won't exceed 50 C. (there is no back boiler involved)

There is a thermal cut out connected to 7 or 8 meters of sensor tube behind the aga, don't know what it's cut out point is at the moment

I am thinking of running all the circuits in 90 C thermosetting

 sockets on 4mm radial  

13 amp oven on 2.5mm radial

20 amp induction hob on 4mm radial

cable ratings, in free air, say 50 C ambient, 

2.5 mm 36A, @50 C = 29A

4.0 mm 49A  @ 50 C = 40A

6.0 mm 63A @ 50C = 51A

at 50 deg C Ca is 0.82 

Its a 3 or 4 inch gap at the back, did think about considering it like conduit but air is free to rise and take heat away, but even if I did the cable rating is still ok.

Parents
  • Not sure about the AGA but in general , if you can keep your wiring below the hot part - the firebox of a solid fuel thing, and the burner tray of a gas or oil burner, the convection that the heater causes works for you rather than against you as at the bottom it is pulling cold air in 

    Being above, in the rising hot air, is to be avoided. Also, whlle you have the drill - where is the ventilation - it is good to be in astream of incoming cool air if possible.

    There is still radiant heat to consider, but any obstacle, but ideally a white painted or metal shiny one,  that breaks the line of sight from the heat source to the cable, will solve that.  A simple L shaped upstand of sheet metal could achieve that - if radiant heat is even a problem ,

    If it is looking marginal, then a test is possible, then to put a couple of the temperature revealing stickers on something like about the size of a jam jar iid one black and one shny, and push the to the back to the proposed cable location, and leave them there for a week, and see what the peak temperature was...

    Mike.

Reply
  • Not sure about the AGA but in general , if you can keep your wiring below the hot part - the firebox of a solid fuel thing, and the burner tray of a gas or oil burner, the convection that the heater causes works for you rather than against you as at the bottom it is pulling cold air in 

    Being above, in the rising hot air, is to be avoided. Also, whlle you have the drill - where is the ventilation - it is good to be in astream of incoming cool air if possible.

    There is still radiant heat to consider, but any obstacle, but ideally a white painted or metal shiny one,  that breaks the line of sight from the heat source to the cable, will solve that.  A simple L shaped upstand of sheet metal could achieve that - if radiant heat is even a problem ,

    If it is looking marginal, then a test is possible, then to put a couple of the temperature revealing stickers on something like about the size of a jam jar iid one black and one shny, and push the to the back to the proposed cable location, and leave them there for a week, and see what the peak temperature was...

    Mike.