Solar PV cable used a AC sub main

Hi ,

I’ve come across an installation where a second consumer unit is supplied via some solar flex 6mm. The consumer   unit is connected to the solar inverter and a garden cabin.

There is no BS number, but it is stamped OLFLEX SOLAR XLS-R  0.6/1KV 6.0 SQ MM

The cable has a stranded conductor, white plastic insulation with a black sheath. 

is it okay to use this cable for AC voltages and does it need to be in containment or would it be considered double insulated?

Parents
  • You mean this?

    The datasheet (and cable marking) says it's rated for 600/1000V for AC, so in theory usable; perhaps consider similar to a double-insulation outdoor-rated version of tri-rated. Whether the installation it conforms to BS7671 will depend on the details e.g. risk of mechanical damage etc.

    Note that the conductors will be class 5 stranded and tinned so may need treatment (ferrules) in terminations, depending on the equipment.

    Lapp say it's UKCA marked so should conform to some standard, but I can't see which on the datasheet. I can't find it on their CPR register either. (Do let me know if you find it)

  • PS Beaten to it, darn telephone! (c: