Due to a change in earthing arrangement, I need to add overall earth leakage protection to a 400 A LV distribution board. The board has an incoming switch disconnector, with overcurrent protection provided by fuses upstream. I can't work out if it would be acceptable for the earth leakage relay to shunt-trip the switch disconnector, or whether I need to replace it with an MCCB. Earth leakage would not implicitly mean that the protective device was interrupting fault current, requiring the CB, but depending on the fault then it could be... Any advice appreciated, ta!

Parents
  • Due to a change in earthing arrangement, I need to add overall earth leakage protection to a 400 A LV distribution board. The board has an incoming switch disconnector, with overcurrent protection provided by fuses upstream.

    What's providing ADS to the submain cable? I would have though it more conventional to have the "RCD" element at the start of each circuit - that also avoids any difficulties in making the incoming cables double/reinforced insulation before the incomer device.

       - Andy.

  • Cheers for your reply Andy - The supply to the board is directly from a DNO cut-out, protected with fuses, via AWA singles. We were expecting TN-C-S and have ended up with TT, hence the need to add the earth leakage protection.

Reply
  • Cheers for your reply Andy - The supply to the board is directly from a DNO cut-out, protected with fuses, via AWA singles. We were expecting TN-C-S and have ended up with TT, hence the need to add the earth leakage protection.