Cat 6 cable specification for domestic house. Do IEE Wiring Regs apply?

I am completely re-wiring by house and taking the opportunity to install an Ethernet network with Cat6 cable. Is such wiring covered by IEE Wiring Regs? Can anyone suggest a specification for such cable? For example do I  need CMP (plenum rated cables) for use in soffits, CMR rated cable when going between floors, or can I just use general purpose CM rated Low Smoke Zero Halogen cables throughout?” It would be useful to distinguish between legal requirement, best practice, common use

Parents
  • This may be deviating off course slightly but the following is worth noting.

  • This may be deviating off course slightly but the following is worth noting.

    Well, have a look at Regulations 21 and 22 ... if you have generation in your installation that operates as a switched alternative to the public supply, or in parallel with it, then BS 7671 is mandatory.

    then it's up to you how much of BS7671 to follow

    Except where the installation has generation (such as Solar PV) operating in parallel with, or a switched alternative to, the public supply, because under those conditions, BS 7671 becomes a legal requirement.

Reply
  • This may be deviating off course slightly but the following is worth noting.

    Well, have a look at Regulations 21 and 22 ... if you have generation in your installation that operates as a switched alternative to the public supply, or in parallel with it, then BS 7671 is mandatory.

    then it's up to you how much of BS7671 to follow

    Except where the installation has generation (such as Solar PV) operating in parallel with, or a switched alternative to, the public supply, because under those conditions, BS 7671 becomes a legal requirement.