This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Cat 6 cable specification for domestic house. Do IEE Wiring Regs apply?

I am completely re-wiring by house and taking the opportunity to install an Ethernet network with Cat6 cable. Is such wiring covered by IEE Wiring Regs? Can anyone suggest a specification for such cable? For example do I  need CMP (plenum rated cables) for use in soffits, CMR rated cable when going between floors, or can I just use general purpose CM rated Low Smoke Zero Halogen cables throughout?” It would be useful to distinguish between legal requirement, best practice, common use

  • A reasonable definition of 'premises' is a house or building, together with its land and outbuildings, occupied by a business.

    I'd suggest that might be a good definition of business premises - in normal UK usage "premises" alone is often applied to domestic as well as commercial property (in the sense of including the whole curtilage, not just the main building(s)).

    and band 2 circuits (220V AC lighting and power)

    The norm in the UK is 230V rather than 220V (and has been since it changed from 240V).

    Using armored cable for three phase and any external underground power/lighting

    There's no real difference in requirements for 3-phase vs single phase - they're both 230V to Earth after all. A 3-phase version of T&E (triple & earth) is readily available and perfectly suitable for indoor use on 3-phase systems (even if in practice it's rarely used for anything other than 2-way switching on single phase lighting circuits).

       - Andy.

  • just a single CAT5 cable running from the router in their basement to a network switch in their bedroom. Admittedly my proposed network is a little more complex, but the point is the same - some common sense is needed.

    Given the increasing use of CAT5/6/7 cable in people's homes

    Been there done that - before we had wifi, I ran a cable between Mrs P's office and mine in order to connect her PC to the router. That became obsolete when we got iPads so I would be surprised if the installation of networks is increasing.

  • Therefore does BS6701 apply to a domestic house? Is there any case law on this issue?

    Yes, the scope of BS 6701 is not limited to any particular class of premises.

    The division of responsibility between the owner and installer is a matter of contract. So if the contract specifies that the telecoms equipment shall be installed i.a.w. BS 6701 and it is not, the installer is in breach.

    I am not clear which specific issue you think might have given rise to case law. The interpretation of "premises" might be context specific, but if there were any case law on its definition (I am not sure that there is) it would simply be the ordinary meaning of the word.

  • Does BS 6701 apply to a domestic house in single occupation? The preamble suggests it only applies to premises - i.e. a house or building, together with its land and outbuildings, occupied by a business

  • that bundles of cables should not mix Band 1 and Band 2 cables and each should be separated in cable trunking (shelves) by 10cm, or put into separate compartments

    BS 7671 says they may be run together if insulated for the highest voltage present. However, agree separation is better all-round.

    BUT

    BS 6701 currently requires at least 50 mm physical separation between indoor telecomms cables and power cables, even if metallic armour, screen or metal containment is used. (For some reason there is no such provision for outdoor cables.)

    Of course 's recommendation of 10 cm meets this requirement.

  • Thanks to all for your contributions some of which I want to expand upon - see below.

    I found a useful summary of BS7671 requirements at:

    My understanding is that Band 1 circuits (data comms, alarm, extra low voltage <50V ac, 120V DC) and band 2 circuits (220V AC lighting and power) must be separated. In the context of a domestic house, this seems to mean that they should not share the same conduit in walls/floors and that bundles of cables should not mix Band 1 and Band 2 cables and each should be separated in cable trunking (shelves) by 10cm, or put into separate compartments. Furthermore there should be protection against premature collapse in the event of a fire; a requirement that could be met by putting cable bundles located above false ceilings in metal trunking. There is also mention of the need to separate electrical cabling from non-electrical services like water pipes though close proximity is permitted if steps are taken to protect the wiring from damage, for example from a burst pipe.

    In terms of the requirements for the cables themselves, it seems that they must be appropriately insulated; >220V for power/lighting and >50v ac for extra low voltage. However, the requirements for safety in case of fire do not seem to be specified in BS 7671, but instead are referenced in BS6701 (as mentioned by gkenyon).  I found a useful summary at:

    It seems responsibilities for the installation of telecommunications equipment and telecommunications cabling are divided between the installer and the owner of the premises housing the telecommunications systems referred to hereinafter as the “premises owner”. A reasonable definition of 'premises' is a house or building, together with its land and outbuildings, occupied by a business. Therefore does BS6701 apply to a domestic house? Is there any case law on this issue? That issue apart, there is sense in me specifying cables that are BS EN 135016 compliant - CPR Euroclass Cca,s1b,d2,a2

    Summary

    Clearly, it is not sensible to apply the same requirements for wiring systems in a factory or office block to the rewiring of my house. Even the requirements for a high-rise block of flats (Grenfell) are very different to those of a three story town house in single occupation like mine. It is unrealistic to expect home owners to spend many thousands of pounds employing consultants to obtain the documentation required by BS EN 13501-6 / 50174 in terms of specification, design, implementation and testing of a cable system that is just a single CAT5 cable running from the router in their basement to a network switch in their bedroom. Admittedly my proposed network is a little more complex, but the point is the same - some common sense is needed.

    Given the increasing use of CAT5/6/7 cable in people's homes it would be useful for the IET to produce a guide on the subject. It should cover the minimum legal requirements to satisfy UK wiring regulations and also suggestions for best practice. In the absence of such a guide I am proposing without the intention to provide any form of professional guidance:

    1. Specifying cable that complies with the legal UK minimum as specified by BS EN 135016
      1. Euroclass Cca (reduced contribution to fire)
      2. Euroclass s1b (smoke production)- more stringent than low smoke, zero halogen (LSZH)
      3. Euroclass d2 (no flaming droplets)
      4. Euroclass a2 (acidity resistance)
    2. Keeping data comms / alarm cable / extra low voltage cables (band 2) separate from three phase, 220V power and lighting (band 1). This means having separate cabinets (though some will need 220V power), separate wall/floor conduits and not mixing band 1 and band 2 in the same bundle so that they can be put into their own compartments in metal trunking fixed to walls above the false ceilings.
    3. Keeping electrical cable separate from water pipes, etc. Ideally they should be put into separate compartments in the ducting between floors.
    4. Using armored cable for three phase and any external underground power/lighting

    I should be grateful for any further comments and suggestions on the above.

  • This may be deviating off course slightly but the following is worth noting.

    Well, have a look at Regulations 21 and 22 ... if you have generation in your installation that operates as a switched alternative to the public supply, or in parallel with it, then BS 7671 is mandatory.

    then it's up to you how much of BS7671 to follow

    Except where the installation has generation (such as Solar PV) operating in parallel with, or a switched alternative to, the public supply, because under those conditions, BS 7671 becomes a legal requirement.

  • This may be deviating off course slightly but the following is worth noting.

  • The legal requirement is to meet all the Building Regulations.  So provided you can get a building inspecter to sign off the work, then it's up to you how much of BS7671 to follow.

  • Data cables are not normally considered to fall within the IET regulations.

    Yes, definitely part of BS 7671 ... but you also need to comply with BS 6701 and its attendant standards, particularly BS EN 50174 series, as referenced by BS 7671.

    So far as I knw, LSZH are not required domestically, but are often used in offices etc, and are therefore widely sold at low prices.

    BS 6701 has more onerous requirements for fire performance of telecomms/ICT cables, than the general case in BS 7671:

    • Fixed installation cables should meet at least EuroClass Ccas1b,d2,a2, in accordance with BS EN 135016.
    • Patch cables (and similar) should meed at least either  EuroClass Eca, in accordance with BS EN 135016, or BS EN 6033212