I am installing a lift in my house. A supplier has specified a 10A MCB to protect a three phase motor with variable speed controller. I am trying to determine the peak current as I have a tight power budget for the building.

The datasheet states "Max RMS acceleration line current, ln" as 15A. I presume this means that under maximum load (at startup, for example) the constant current that yields the same power dissipation as the time-averaged power dissipation of the AC current is 15A per phase.

This implies that 15A passes through the MCB for at least a complete cycle (50Hz = 20mS) - i.e. time-averaged. Is there a danger that a 10A MCB would trip if 15A was passed through it for 20mS? What is the tripping time of a typical MCB? Do I need to specify a special type of MCB for such use?

In terms of calculating the peak  power consumption of the three phase circuit should I use 15A per phase with line to line voltage of 400VAC? The datasheet specifies the main supply voltage as 3x400VAC @ 50Hz.

Parents
  • MCBs have two tripping elements - magnetic which operates near "instantly" and thermal - which usually take from several seconds to minutes or hours. The trip threshold of the magnetic part depends on the "type" of the MCB (B, C or D) - common B types have a threshold of between 3x and 5x the MCB's rating - so a B10 shouldn't trip instantly on less than 30A.  The thermal part will trip at different speeds depending on the magnitude of the current - at 1,13x it shouldn't trip in less than an hour. and even at 30A it'll likely take over 10 seconds.

       - Andy.

Reply
  • MCBs have two tripping elements - magnetic which operates near "instantly" and thermal - which usually take from several seconds to minutes or hours. The trip threshold of the magnetic part depends on the "type" of the MCB (B, C or D) - common B types have a threshold of between 3x and 5x the MCB's rating - so a B10 shouldn't trip instantly on less than 30A.  The thermal part will trip at different speeds depending on the magnitude of the current - at 1,13x it shouldn't trip in less than an hour. and even at 30A it'll likely take over 10 seconds.