This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

TT’ing external socket - series RCDs

Hi,

Following on from a previous post, I wanted to ask this separately for clarification as I usually TT distribution boards as a whole.

25A radial circuit leaves internal DB and loops between various sockets and FCUs (without integrated RCDs) within garden connected to the buildings PME supply. The “final” socket, away from any other class 1 appliances, has its CPC terminated in a plastic enclosure, with this socket then connected to a local earth rod. This socket also has a built in, 30mA RCD.

Does this comply with regulation - I think it does, but wanted to check. Generally I would TT a DB externally, however cost is an issue here. I don’t foresee this being any different than an EV charger with its own earth rod, and the PME disconnected. 

Does having 2 RCDs in series, cause any other issue than nuisance tripping? The house RCBO would likely trip at the same time as the RCD socket within the TT island. This is I think offering a belt and braces approach with redundancy. 

This far end socket will be used for a blow up hot tub, every now and again, and needs to be energised whist in use. It doesn’t make sense to install a dedicated supply for this, and it’ll be too costly. 

Thanks. 

Parents Reply Children
  • I think vantech is referring to installing a supplementary earth rod to each DB. Which of course doesn't make it TT.

    BTW Chris, I heard a podcast recently about black holes and dark energy here share.fireside.fm/.../2YAGasSP QG0ltBCi seems to be from you, are you a dark horse?

  • I mean if I TT, it’s generally done at a DB, not at the electrical socket/accessory itself. I prefer PME any day over TT.