TT’ing external socket - series RCDs

Hi,

Following on from a previous post, I wanted to ask this separately for clarification as I usually TT distribution boards as a whole.

25A radial circuit leaves internal DB and loops between various sockets and FCUs (without integrated RCDs) within garden connected to the buildings PME supply. The “final” socket, away from any other class 1 appliances, has its CPC terminated in a plastic enclosure, with this socket then connected to a local earth rod. This socket also has a built in, 30mA RCD.

Does this comply with regulation - I think it does, but wanted to check. Generally I would TT a DB externally, however cost is an issue here. I don’t foresee this being any different than an EV charger with its own earth rod, and the PME disconnected. 

Does having 2 RCDs in series, cause any other issue than nuisance tripping? The house RCBO would likely trip at the same time as the RCD socket within the TT island. This is I think offering a belt and braces approach with redundancy. 

This far end socket will be used for a blow up hot tub, every now and again, and needs to be energised whist in use. It doesn’t make sense to install a dedicated supply for this, and it’ll be too costly. 

Thanks. 

Parents
  • but IEV does define 'island' as a term for use in a power system:

    Humm, Depends how you interpret the brackets - I would have read "island (in a power system)" as "in a power system, the term 'island' means..." rather than the term 'island' may only be used in the context of power systems.

    so metaphorically speaking, an "island" in a sea of connected-mode installations all around.

    Indeed - but to my mind the same metaphor works just as well with earthing systems - the consumer's TT installation as its own little refuge of true earth in a sea of PME...

    I'd see no contradiction if we were to have:

    island (in a power system) ..., and

    island (in an earthing system).....

    in the same sense that in BS 7671's own definitions we have:

    "Central power supply system (low power output)" which clearly doesn't restrict the use of the term "Central power supply system" to just the context of low power output.

        - Andy.

  • Indeed - but to my mind the same metaphor works just as well with earthing systems - the consumer's TT installation as its own little refuge of true earth in a sea of PME...

    But that would require separation from the PME (8 to 10 m all-round, including underground), and we don't know what's underground connected to PME.

    A closer analogy in urban areas where you can't get proper separation would be a TT pontoon bobbing up and down on the PME GPR (generally low, but can get choppy). Not that you'd necessarily feel anything because you might be bobbing up and down with it ...

    So, I'm not sure the concept is really appropriate to earthing in urban areas ... certainly not helpful.

Reply
  • Indeed - but to my mind the same metaphor works just as well with earthing systems - the consumer's TT installation as its own little refuge of true earth in a sea of PME...

    But that would require separation from the PME (8 to 10 m all-round, including underground), and we don't know what's underground connected to PME.

    A closer analogy in urban areas where you can't get proper separation would be a TT pontoon bobbing up and down on the PME GPR (generally low, but can get choppy). Not that you'd necessarily feel anything because you might be bobbing up and down with it ...

    So, I'm not sure the concept is really appropriate to earthing in urban areas ... certainly not helpful.

Children
  • pity, as 'ground island'  is a common and well understood phrase among my RF colleagues, and seems to be understood in pulse power circles too. Perhaps it is just the company I keep ;-)

    Also 'island' is used in PCB layout when the ground-plane is cut and tabbed  (creating a region on layer on on a mezznine on a layer above or below that connects to the plane on one edge or corner only ) so cross currents in the main plane do not introduce unfortunate gradients in delicate circuits, The classic example seen in every mobile phone being a PLL with many MHz/volt of VCO tuning on a transmitter board with a PA. On a solid ground-plane the PA keying on twangs the oscillator as the large transmit current introduces many tens of uV between adjacent ground vias on the PCB- but if the PLL is on its own ground island, then the tuning and gnd Iines of the VCO  are not pulled in this way, and the frequency is un-modulated.  This EMI problem and solution is very close to the power situation.

    There is a lot of technical vernacular that is not ideal, but if it accelerates getting a complex idea across to those in the know with as few words as possible, it is likely to stay in common use.  The best that the ever-stretched standards teams can do in that case is probably to run behind the new lingo and add to the glossary as required.

    M