Plug/socket earth pin length

Hello,

The earth pin on UK plugs and industrial IEC EN 60309 connectors are longer to make the earth connection first and break last. This seems sensible but i have a question

I have several 19" rack enclosures that require interconnecting with power and control circuits.  I cannot fit a typical power connector (eg 60309) but instead have found many other circular power connectors (eg Mil-spec) that are adequately rated and with designated earth pins, however, the earth pin is invariably the same length as the live pins i.e. the earth will not make first break last. This equipment is for use indoors, sockets less than 32A and with added protection with an 30mA RCD.

My understanding is that a longer earth pin is required under BS7671 but I can't actually find it stated explicitly any where in the regs. I'm probably not looking hard enough or is this a myth??

Can anyone point me to the regulation in BS7671 or other guidance notes where it states the earth pin must be longer than the live pins of a power connector? or is this implied where BS7671 states the use of IEC 60309 connectors - and it is in that standard where it states the earth pin must be longer? And just to be sure, would you agree that the use of 60309 connectors is not a requirement for indoor installations, but is for outdoor installations?

Thanks

Parents
  • Without knowing the type of equipment, ir's difficult to properly advise, because other standards may well apply. For example, if the equipment is part of Machinery as defined in the Supply of Machinery (Safety) Regulations then BS 7671 does not apply at all to these interconnections, but BS EN IEC 60204-1 does.

    If it is within the scope of BS 7671, then BS 7671 requires electrical equipment to comply with the latest British or Harmonized standard ... or the installer has to ensure "at least as safe" as, at a minimum, relevant provisions in BS 7671 (See Section 511) ... in the case of plugs, socket-outlets, and couplers (e.g. to BS EN IEC 60320), that are referenced in the general requirements (Parts 1 to 6) of BS 7671, most , if not all, have a longer protective conductor pin, and therefore it could be argued that you'd have a bit of a job covering 'at least as safe' without looking at the complete risk assessment of withdrawing or uncoupling the particular connectors you are looking at. However, if you have to operate an isolator before you have access to remove the plug, for example, that might be considered equivalent safety.

Reply
  • Without knowing the type of equipment, ir's difficult to properly advise, because other standards may well apply. For example, if the equipment is part of Machinery as defined in the Supply of Machinery (Safety) Regulations then BS 7671 does not apply at all to these interconnections, but BS EN IEC 60204-1 does.

    If it is within the scope of BS 7671, then BS 7671 requires electrical equipment to comply with the latest British or Harmonized standard ... or the installer has to ensure "at least as safe" as, at a minimum, relevant provisions in BS 7671 (See Section 511) ... in the case of plugs, socket-outlets, and couplers (e.g. to BS EN IEC 60320), that are referenced in the general requirements (Parts 1 to 6) of BS 7671, most , if not all, have a longer protective conductor pin, and therefore it could be argued that you'd have a bit of a job covering 'at least as safe' without looking at the complete risk assessment of withdrawing or uncoupling the particular connectors you are looking at. However, if you have to operate an isolator before you have access to remove the plug, for example, that might be considered equivalent safety.