Unearthed buried armour. C2 or C3

Hi Guys

On a domestic EICR i have come across a 3 core swa cable that loops to various points down the garden where the armour has just been cut back so obviously the armour itself is not earthed. The cable is buried.  I have initially coded it as a C2 but am doubting myself.  Is it immediately dangerous or is a C3 more appropriate.  The installation is TT with 30m/a rcd protection.

Thoughts please

Gary

Parents Reply Children
  • Yuk! Thank you for the picture, which I had not seen earlier.

    In fairness to the householder (or any other lay person), it is not obvious how to install SWA. At least in this case, the armour might protect against a spade if not a fork.

    Given the L-E reversal, I conclude that there is at least a CPC in the cable.