This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Max ZS

Sorry maybe a silly question but...

I have the house DB TT install -  Ze at 0.38ohms with a high current 2 lead test.

Sub-board 35 meters away, with it's own earth stake. Zdb with a 3 lead low current test is 20.0 ohms.

All circuits off the sub board are relatively short and the Zs tests are around 20.0 - 21.1 ohms. 

Should the max Zs on the test cert be 1667? As electraform Zs test results are in red as the readings are above max Zs levels for the RCBO's 

TIA

Parents
  • Depends on the rcd protecting individual circuits. If 30m/a then yes.

    Gary

  • Hi Gary. Yes all circuits are on an RCBO 

Reply Children
No Data