Sorry maybe a silly question but...

I have the house DB TT install -  Ze at 0.38ohms with a high current 2 lead test.

Sub-board 35 meters away, with it's own earth stake. Zdb with a 3 lead low current test is 20.0 ohms.

All circuits off the sub board are relatively short and the Zs tests are around 20.0 - 21.1 ohms. 

Should the max Zs on the test cert be 1667? As electraform Zs test results are in red as the readings are above max Zs levels for the RCBO's 

TIA

Parents Reply Children
  • "Sub-board 35 meters away, with it's own earth stake."

    I did wonder if the main installation was actually TN rather than TT though - 0.38Ω does seem implausibly low for a TT system (or the test had been done other than with consumer's end of the earthing conductor connected to nothing but the meter).

       - Andy.

  • Yeah i know what you mean. Definitely TT though

    Did the Ze with a high current 2 lead test and main earth removed at origin

    Tested board in the outbuilding with everything connected 3 lead low current and got 20 ohms.

    I just thought the Ze  was a better reading because of the high current test

  • More than wanting an explanation for the low Ze, I was curious to know why there was such a big difference when r1 + r2 of the distribution circuit must be of the order of one tenth of an Ohm.

  • As I read it, the remote DB has its own independent earthing arrangement ("it's own earth stake") - so the loop isn't going through the distribution circuit's R2 or indeed the main installation's earthing arrangement (whatever it turns out to be).

        - Andy.